Being asked now to begin plan checking residential PV systems, since I have 34 seconds a day in free time. :lol: I am having trouble wrapping my head around this, and could use some help.
Per 2008 nec, section 690.53, a label must be posted with calculations for:
1. rated maximum power-point current
2. rated maximum power point voltage
3. maximum system voltage
4. short-circuit current
5. Maximum rated output current of the charge controller [if installed]
What formulas or calculations do I use to find the correct answers? Typically, as an inspector, the only information I had looked at on the module spec sheet in the field was verifying the correct module was installed. I have never done the calculations.
Here is what I think I understand and the calculations I am proposing to use [drama starts Monday!:thumbsup:]:
1. --PP current - IMP*156%=PP current for that series string, then add all series strings to get the total PP current.
2.--PP voltage - Vmp per module* number of modules in the string with the most modules = PP voltage, assuming all strings are series strings.
3. Max sys volt --- Voc per module*number of modules in the string with the most modules* temp coefficients from module specs if given OR correction factor for ambient temp [for crystalline and multicrystalline modules per 690.7] again, assuming all strings are series strings.
4. short-circuit current -- Voc*156%= short-circuit current for each series string, then add all series strings to get the total PP current.
5. . Maximum rated output current of the charge controller [if installed]. --clueless as to formula!
Am I right on at least some of these? Any information, comments, or suggestions would be greatly appreciated.
Thanks -
Per 2008 nec, section 690.53, a label must be posted with calculations for:
1. rated maximum power-point current
2. rated maximum power point voltage
3. maximum system voltage
4. short-circuit current
5. Maximum rated output current of the charge controller [if installed]
What formulas or calculations do I use to find the correct answers? Typically, as an inspector, the only information I had looked at on the module spec sheet in the field was verifying the correct module was installed. I have never done the calculations.
Here is what I think I understand and the calculations I am proposing to use [drama starts Monday!:thumbsup:]:
1. --PP current - IMP*156%=PP current for that series string, then add all series strings to get the total PP current.
2.--PP voltage - Vmp per module* number of modules in the string with the most modules = PP voltage, assuming all strings are series strings.
3. Max sys volt --- Voc per module*number of modules in the string with the most modules* temp coefficients from module specs if given OR correction factor for ambient temp [for crystalline and multicrystalline modules per 690.7] again, assuming all strings are series strings.
4. short-circuit current -- Voc*156%= short-circuit current for each series string, then add all series strings to get the total PP current.
5. . Maximum rated output current of the charge controller [if installed]. --clueless as to formula!
Am I right on at least some of these? Any information, comments, or suggestions would be greatly appreciated.
Thanks -