This what the NEC says:
408.58 Panelboard Marking. Panelboards shall be durably
marked by the manufacturer with the voltage and the
current rating and the number of phases for which they are
designed and with the manufacturer?s name or trademark in
such a manner so as to be visible after installation, without
disturbing the interior parts or wiring.
There are other requirements for stuff also: High leg identification, fault current, etc....
I guess if the cabinet and interior is the only one the cover fits then it is probably acceptable.
Often times they make one box and or cover that is for more than one interior panelboard. If that is the case the label will have to include information for all the possibilities, and can be confusing to identify which unit you have.
There were stampings inside the "cabinets" (I think I now have the proper term) - at the tops. Was the only marking inside. The cover door sticker "label" appeared to match. Though after reading other posts, there could be other cover that fit. Does this apply to Siemens products (these cabinets were relatively new - within last 10 years or so)?
I agree!!!Check UL's labeling requirements for a listed panel cabinet, bussing, and trim.
Not saying anything, but improper labeling is often a sign of 'gray market' products.
I was also told not get cars from the early shift on Monday after the big Sunday game.:happyno:Or the late shift on Friday made it![]()
it looks like GE (good enough) electrical breakers, but what i am wondering is this in a house or apartment complex only 3 branch circuits, what the heck????