I am working to try to get a contractor out of a bind. They have installed non-TC rated cable within a cable tray and it would be very costly to remove and replace the cable with new TC rated cabling. We are weighing two options, either:
-Enclosing the entire cable tray with an enclosed wireway
-Or installing the non-TC rated cabling within an enclosed wireway on top of the cable tray.
These both appear to be NEC compliant solutions. Does anyone agree or disagree? Has anyone else run into this situation before?
-Enclosing the entire cable tray with an enclosed wireway
-Or installing the non-TC rated cabling within an enclosed wireway on top of the cable tray.