Can SO cable labeled TC be used outside of a cable tray? Or is it limited soley to cable tray?
Sorry, I misspoke. Can cable labeled TC be used outside of a tray? I have a cable I want to use for a wind turbine in free air, no tray. The label is:
TC-ER THHN/THWN 90C Dry 75C Wet 600V Sun Res Oil Res I/II DIR BUR E171371 or MTW or DP-1 or WTTC 1000V Dry or Submersible Pump Cable or ......
Make sense? The inspector general says it needs to be in a tray.
I don't believe the THHN/THWN rating changes compliance for the OP-er's desired usage, i.e. in free air.Is it a cable or a single conductor? If it is a single conductor, then the marking indicates it is also rated as THHN or THWN. In that case you can use it in the same way you could use THHN or THWN wire.
That is correct... when conductor(s) are outside, but...Article 225 Outside Branch Circuits and Feeders Part I General covers how you can use individual conductors.
No flaw... just not the prescribed-by-others logic...
Where is the flaw in that logic?:?