wirebender
 - North Central Texas
Is there anything in the NEC that would prohibit the use of the high leg to supply a single phase load such as a water heater?
Don't think so, at least as long as it is on the right kind of breaker, but why would you want to?
You mean a load that is single phase that uses two hots on 208V but you use a single breaker on a high leg system with a neutral?
I don't think there is anything in the code that says you can't use it line to neutral for a 208 volt load. I know it is not a good electrical practice, but I don't think the code says you can't.
Yes, the OCPD could be an issue, but that is not a direct restriction on the use of the high leg for line to neutral loads. (I could always use a fuse for the OCPD)I think the problem lies in trying to do so with a single pole breaker with a 208 v rating.
(assuming one is not using a 277v panelboard)
Do they even make a single pole 240 volt breaker?
I looked in the SQUARE-D book but couldn't find a breaker that is rated for 208V. What is the rating of breaker that is used on 277V lighting?
Breaker issue aside, Will the load work if it was designed for 2 pole 208V but it is connected to single pole 208V?
277 volt. Problem is a 277 volt breakers are not designed for installation in a 240/120 panel.
If you happen to have a 480/277 panel on the 240 system, you could use a SP 277 breaker.
You can. The voltage is not the issue. The well tailored hound has it right.I don't understand. If it is designed for 277 why can't it be used on lower voltage? I assume it is listing issue?
If you happen to have a 480/277 panel on the 240 system, you could use a SP 277 breaker..
well tailored hound