The Energy Trust Of Oregon requires any pv system that has batteries attached to have a 5 jaw meter. I can find the socket but not the meter. Has anyone seen any of these for sale?
The Energy Trust Of Oregon requires any pv system that has batteries attached to have a 5 jaw meter. I can find the socket but not the meter. Has anyone seen any of these for sale?
I'm assuming the meter is required for RECs or something similar, and is distinct from the service (net)meter.
What I don't understand is why batteries make any difference to the type of meter required. Just curious if anyone knows why.
The 5 jaw meter will be a 12S meter. Usually reserved for single phase services fed from a three phase bank. Why isn't the POCO supplying one?
It appears that a 5 jaw meter, which is a 12S, is for a 3 Phase application. This will be installed in a single phase home. In Oregon the POCO replaces their meter with a net meter. Then we are required to install another customer owned watt hour meter in addition. I'm not sure what difference the batteries make.
It appears that a 5 jaw meter, which is a 12S, is for a 3 Phase application. This will be installed in a single phase home. In Oregon the POCO replaces their meter with a net meter. Then we are required to install another customer owned watt hour meter in addition. I'm not sure what difference the batteries make.
Code:
What is the purpose of the customer owned watt hour meter, and where is it installed?
OK makes sense, why is it required? I can see it being highly desired but don't see why an outside party would require it. Also why would 5 jaw meter be needed? This would have to be on load side of an inverter that is not shown in your link, and I see no reason why typical 4 jaw meter would not work if it is typical 120/240 single phase.
The picture is a simplification of the system. Did you read my post about the way the meters are configured? or the one regarding the RECS?
One meter can be used for net metering, but with a battery backup, a 2S meter will stop while the battery is supplying loads and the generator is exporting. The 12S is needed to measure all production with a battery backup.
The outside party is the one responsible for taking care of their REC's not the POCO. It is their meter that they have to record these REC's with. As with any tradeable commodity, you need a record.
Please tell me what REC stands for. ...
Why is energy sold going to be differerent from the results of net metering?
When it comes to trading commodities and measuring devices the accuracy of the device is strictly regulated. Just look at scales used for sale of goods or meters at fuel pumping stations - who verifies this privately owned meter is accurate?
Finally! After going through all the files on my puter, the mags laying around, then googling for anything to help, I found the perfect article on the good ole web... Look at page 22We have one installation with battery backup on our system and had to learn some things the hard way...