Looking for a little advise, I have been asked to install a 2 pole 20amp gfi breaker for a pool pump. The pump is straight 240v no neutral, what should or should not be done with the load neutral terminal on the breaker?, should the breaker neutral wire get connect to the neutral buss in the panel?
 

masterinbama

Senior Member
Looking for a little advise, I have been asked to install a 2 pole 20amp gfi breaker for a pool pump. The pump is straight 240v no neutral, what should or should not be done with the load neutral terminal on the breaker?

Nothing





should the breaker neutral wire get connect to the neutral buss in the panel?


yes
 

iwire

Moderator
Staff member
Location
Massachusetts
The neutral pigtail on the breaker must be connected to the panel neutral.

The neutral terminal on the breaker will remain unused.
 

chris1971

Senior Member
Location
Usa
The grounded conductor on the breaker should be connected to the grounded buss so the breaker will work when you press the test button.
 