My experience seems to be limited with the project I am currently bidding. I am about to show my ignorance and embarass myself with this question but I have to have it answered even if I loose face with this question. I am a residential repair electrician, mainly fire damage for insurance companies, I am bidding a project that has to have a new service. It is an 8 pack apartment building. I propose to install two 4 gang meter packs with seperate feeds to the power companies pad mounted transformer 75 linear feet from the location of the meter packs. I proposed running two seperate parallel service feeders to these banks using 4/0 THHN conductors. The inspection department has failed my drawing because I didn't figure in the Temperature Correction Factor. 4/0 THHN is rated at 260 amps. Miltiply that by 2 (parallel) and you get 520 amps. I'm in Southeast Texas and it gets hot down here. It's not uncomon for temperatures to reach 105 in the summer. I honestly have never had to figure a service like this before. I know how to do the calculation using 310.15 (B) 16. But how do I determine the Ambient Temperature of my particular location in order to satisfy the electrical inspection department? Any correction factor that I use at this point will be a guess. Could someone point me in the right direction?