Good friend has a house down at the beach, complained of the gfci breaker occasionally tripping. breaker feed 3 outside recepticles. So I drive down and check and the salt water/air has had good sucess rusting out the screws and yokes of the recpticles. I cut the wire on all 3 recpt and replace the recpt and the PVC boxes and covers (screws in yoke broke off or so rusty could not turn them). Total circuit length had to be less than 100' of 12 awg romex. After I replaced i took my hypot and checked with test parameters of 200vac 3 seconds, with a trip of 5ma ( could not remember what a breaker would trip at. hypot showed .53 - .59 ma leakage from hot to neut/neut to grd/ hot to grd.
1) what should the breaker trip at
2) should I be concerned about the quality of the wire with this amount of leakage
I know .5ma is a very small amount but it was only 200volts. I would have thought there would be no leakage at this voltage level.
Never used a hypot to test a recpt circuit, have used it alot at work checking parts we manufacture.
Travis
1) what should the breaker trip at
2) should I be concerned about the quality of the wire with this amount of leakage
I know .5ma is a very small amount but it was only 200volts. I would have thought there would be no leakage at this voltage level.
Never used a hypot to test a recpt circuit, have used it alot at work checking parts we manufacture.