petersonra
- Northern illinois
- Semi-retired engineer
Something that occurred to me.
I wrote an email some time ago that I never actually sent.
I mentioned that the EGC is sized according to the OCPD, and that in some cases such as with motors, the OCPD is larger than "normal" so the EGC needs to be larger than the ampacity of the protected conductors might otherwise indicate.
In thinking about this, I asked myself a question. How would this apply to motor circuit protectors? They are the sole SC protection for a motor circuit that has an MCP, so would not the same thing apply in such a circuit? I am suggesting it appears like for motors using an MCP you would have to always size the EGC at the same size as the main conductors.
But, I can't say i have ever seen anyone actually do this. Am I missing something here?