Questions on MV transformer clearances and egress requirements.

Status
Not open for further replies.

patrox2000

Member
Location
Baltimore, MD
Hello everyone,

I have 15KV primary - 480Y/277V secondary transformer and then I have a fence around it. I only have 22-3/4" of space on each side of the transformer and 3'-0" on the back and 7' on the front. the fence only has one door in front of the transformer.

Q1: where in the NEC are the requirements for space clearances on the sides and back of a medium voltage transformer? i have heard it is 2 feet on the sides and on the back but haven't been able to find this in the NEC.

Q2: Are the clearances above ok for egress? (NFPA 101) i have heard this is 36" but haven't been able to find this either.

Thanks.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Are there any exposed parts on the back of the equipment?
Does any routine maintance need to be done on the rear of the transfromer while it is energized?
Is the primary under the control of a utility?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
It would help more to know who owns the transformer. Where is the point of delivery?
 

Phil Corso

Senior Member
Patrox... A large HPI company I worked for required:
a) An 8-foot high fence.
b) 48-inch minimum distance between the fence and HV terminal side.
c) 36-inch minimum distance between the fence and the other 3 sides; and
d) At least two access gates on opposite sides of the fence!

Regards, Phil
 

ron

Senior Member
I guess it depends on the type of design. I have a dry type 500kVA 480V-4.16kV transformer in a SWGR room next to everything leaving the required working distance per Chapter 1 in the NEC.
 

patrox2000

Member
Location
Baltimore, MD
Are there any exposed parts on the back of the equipment?
Does any routine maintance need to be done on the rear of the transfromer while it is energized?
Is the primary under the control of a utility?

Jim, the responses to your questions are 1) no, 2)no, 3) this is for a university campus, so it will be a campus feeder connecting to the transformer primary.

i was just wondering where in the NEC the clearance requirements for an oil filled transformer were and if there were any NFPA requirements for egress from an electrical equipment courtyards. if anyone knows the answers please reply.

thanks.
 