Set-up:
GE Frame 7FA turbine, with Fast start Isolation Transformer, 5450KVA, 4160V HV side, with split secondary with a delta and Y winding both rated at 2725KV, 2080V.
This transformer feeds power to the GE LCI system. I am trying to determine how to come up with the criteria for properly sizing the MV cable on both the HV and LV sides. I have seen multiple installations and it appears every designer has a different approach (no consistency). I can't find any GE documentation other than one job it said it needed to be capable of 8000KVA and another that said 8500KVA for back to back starts. And they state some capacitance issues and criteria if there was no ac line reactor.
Anybody experienced with these cable requirements?
Would appreciate input.
GE Frame 7FA turbine, with Fast start Isolation Transformer, 5450KVA, 4160V HV side, with split secondary with a delta and Y winding both rated at 2725KV, 2080V.
This transformer feeds power to the GE LCI system. I am trying to determine how to come up with the criteria for properly sizing the MV cable on both the HV and LV sides. I have seen multiple installations and it appears every designer has a different approach (no consistency). I can't find any GE documentation other than one job it said it needed to be capable of 8000KVA and another that said 8500KVA for back to back starts. And they state some capacitance issues and criteria if there was no ac line reactor.
Anybody experienced with these cable requirements?
Would appreciate input.