There was a incident awhile back where a 20amp circuit faulted to light fixture or conduit . circuit was at 277v feed out of a 100a panel which came from a mcc bucket , mcc was fed with 500a cb w/gf protection. 500cb came from the switchgear .
When the fault happened it carried back to the switchgear 500a cb and tripped [ it bypassed 3 molded case cb till the 500a @ SG ]. This caused the mcc to trip and building to shut down.
Besides having a cordiation study completed does anyone believe the lighting circuits or lighting panel should have GFP in the mean time ?
Or something else ? THANKS.