First off, I can't answer a lot of your questions. I have not been involved in design with the listed constrainsts. And I do little design work. But, perhaps I have some ideas that will help.
Assumptions:
1. I'm guessing you are not the engineer-of-record, but rather one of the design team. Why does this matter? Well if so, you are not making policy decisions, but rather following directives. This is okay, it actually narrows down the options available.
2. The equipment is to be powered from a 60Hz utility connection.
3. The project is big enough that the existing plant can add a 2011Hp motor to the existing system, or if a new plant, the utility is included in the planning.
4. Project is industrial, not commercial - not open to the public, not waste water, not potable water.
... I have a very large (2000hp+) motor that requires 690V. We are in the early design process and the motor HAS to be 690V. ...
... Is there some kind of IEC equipment that I can use? ...
... What code issues will I run into? ...
As noted by others:
2000Hp at 690V really sucks.
1700A X 1.25 = 2100A
Thats a lot of copper.
As for the IEC equipment, I wouldn't worry about it. This is a non-trivial project. Your not going to cheap it out. You're going to design a safe, reliable, cost-effective system. I'd be certain that is what is what your customer wants.
Get rid of this whole idea of code issues. The NEC is a set of minimums that is not guarenteed to work well or efficiently, may not burn down, and should not shock you too easily. It is not about design, and it has very little guidance for systems above 600V. Once you meet "safe, reliable, cost-effective", any code issues are generally legal trivia.
... I don't know what type of shielding I need to be honest. I think it will not be made for VFD. It has to be very heavy duty. All I know is that we will need it. I'm kind of inexperienced in cable shielding specifications. ...
hamm -
It's time to get some help. You are not going to spec this with intenet gossip. If your design group does not have the expertise, you will have to hire it.
... Maybe the AHJ would accept a design that has your seal on it in lieu of a listing.
It's rare an AHJ has much to say about complex, high power, industrial design. They generally don't have the expertise available to judge. One exception is local requirements on listed equipment. I've worked a few jurisdiction where the AHJ insists on listings far in excess of NEC requirements. Morons or not, they have the badge and the gun - I generally say, "Yes Sir!"
... do I need to use medium voltage switchgear housing or low voltage?
These are on the accounting end (cost-effectiveness) of the design issues.
I'd probably look at taking the service at 13.8KV or 4.16KV, using either 15KV or 5KV equipment. Do the motor starting and protectiving relaying at the MV. Put a MV primary Delta/ 690V Delta transformer between the motor starter and motor, maybe 4MVA - depending on motor starting load. Probably have to put GF on the Delta secondary to watch for motor faults.
Or
Take the service at 480V, 3000A, 65KA - 100KA equipment, protective relaying at 480V, 480d/690D transformer feeding the motor, Same GF on delta secondary.
But, this is just my internet gossip - no better than anybody else's, and certainly nothing I would rely on.