I'm using 65?C rise to maximize my ampacity rating. I have absolutely no vendor data on the installed bus. The vendor manual is scant to say the least. The interpolation is the midpoint between the .25 x 1 and the .25 x 1.5. This gives me the 740A. Interpolation using Excel and AC ampacity vs surface area gets me within 1% error of this value.
I don't believe I can say that AC and DC curent ratings would be equal because of the nature of the beasts. AC has the nice zero crossing. If I look at average current which would equate to the DC, they will not be equal.
Integrate the sine wave over a period of 0 to 2PI and then devide by 2PI to get average current. This is, as I understand it, the equivalent DC for the given AC current. That tells me that a bus rated at 1000A AC will be rated at 637A DC. This is bad for what I'm trying to do, but I don't see any way around this. From paragraph 1 this means, again as I understand it, that my bus is rated at 471A. This is bad.
Looking at heating (I2R), using the RMS of the AC current and the equivalent DC (as calculated above), the AC will produce a greater heating. If copper bus is sized based partially on the heating effects of the current, then I can take a small credit for this, but probably not enough to cover my bum.
When my plant goes black and everything is loaded onto the batteries, my bus has to be able to handle 658A (for the first minute). After this, load shedding takes care of most of the problems. But for that minute, things are going to be toasty. Given the size of the bus, I don't see any way to justify saying it is rated appropriately.