- New Jersey
- Journeyman Electrician (retired)
It falls under:
(3) A listed electrical circuit protective system with a minimum 2-hour fire resistance rating. The
installation shall comply with any restrictions provided in the listing of the electrical circuit
protective system. Also the 6 feet falls under 110.3b manufacturer requirement.
Take a look here:http://www.datatechtx.com/pdf/lifeline/FPU-05.pdf
Thx
Is it me or could they have worded this better? A listed electrical circuit protective system doesn't sound much like 2 hour rated conductors installed in EMT.
I didn't see the 6' requirement in that pdf you posted.