What would cause the motor for an aerating system to overheat? The voltage was correct, but they ran it without a hose connected to it for 7 minutes apparently...with no load would the motor overheat?
You haven't told us anything about what type of motor it is nor anything about the type of pump its drivin and how. It would be nice to know the voltage, 1ph or 3ph, the HP etc. Providing such information would be helpful in getting an answer that is relavent to you application.
The motor is used to pump air through a 2" hose to aereate a water supply. The motor is single phase 230volts, 6.5 amps with a 250volt standard plug. The rotation was correct, no single phasing, but owner plugged in for 7 minutes connected to a long air hose with nothng attached to it. For moving air I would have thought no need for overloads, but for maimum protection an motor controller would have helped. Since factory 240volt plugs are not to be cut off, do we install an 240volt receptacle with motor controller for an Regenerative Blower motor? Was too long a hose the cause of overheating?..or lack of some backpressure?
No back pressure means more volume of air will be easily moved. More volume of air moved means more load on the motor. Your motor was not unloaded but infact had even more load on it when not connected to create some restriction on the blower output.
Proper overload protection on the motor should shut it down if it is drawing too much current, does not matter that the motor is in the airstream. Yes the motor in the air stream helps keep it cooled but if motor is overloaded to begin with that only helps to a certain extent, but is still possible to overheat windings if enough load is present.