Ron Hill
Member
- Location
- Cleveland Ohio
Is there any requirement that ground tails have to be THHN?
Why wouldn't they be solid copper?Is there any requirement that ground tails have to be THHN?
Why wouldn't they be solid copper?
Is there any requirement that ground tails have to be THHN?
Is there any requirement that ground tails have to be THHN?
Do they make solid THHN :? When ever I went to a supply house and asked for THHN, they never said "solid or stranded?":? What does solid copper have to do with THHN?
Do they make solid THHN :?
Do they make solid THHN :?
Well, I'll be tared and feathered :ashamed1:Let me rephrase: What does copper have to do with THHN? It comes in AL also, stranded to boot.
Do they make solid THHN :? When ever I went to a supply house and asked for THHN, they never said "solid or stranded?"
Well, I'll be tared and feathered :ashamed1:
310.106 Conductors.
(C) Stranded Conductors. Where installed in raceways,
conductors 8 AWG and larger, not specifically permitted or
required elsewhere in this Code to be solid, shall be
stranded.
As the NEC is a permissive code, this permits solid wire of size 10 AWG or smaller. I have certainly seen 12 AWG and below THHN in solid. Most of 10 AWG I've seen is TW or more ancient.