Code allows a 70A-3P breaker at 250% FLA for a compressor I'm installing. How likely am I to experience startup problems if I put it on a 60A-3P breaker?
Code allows a 70A-3P breaker at 250% FLA for a compressor I'm installing. How likely am I to experience startup problems if I put it on a 60A-3P breaker?
Very hard to predict, but I will say that if it is a reciprocating compressor they are notoriously hard to start. They have a large mass and high resistance to overcome.
Do you understand that you can use the 70 amp breaker even if the conductors are not rated 70 amps?
Great response! Just what I was looking for! FLA is 28A x 13 = 364A. So it looks like a 60A breaker "should" hold. The customer's compressor guy never came - maybe today...