I'm installing a piece of testing equipment that has a 10 HP/240v-3P motor. There is no equipment nameplate and the manual refers you to the motor's. This equipment has been factory wired to the line side of a small VFD using a flexible cord, but no plug.
The equipment is on castors, so is it more common to install a plug on the cord with a receptacle? Or would hard-wiring be the preferred method?
What qualifies equipment or motors for cord and plug?
Would hard-wiring violate 400.8(1) or does this qualify for "frequent interchange" in 400.7(A)(6)?
For conductors: I've figured Table Amps (28A) X 125% = 35A. The conduit will have 7 current carrying conductors, so after derating 70%, it seems I need 3x#8 THHN.
For OCPD: It's fed out of a standard panel with a Cutler Hammer type BA breaker (inverse time right?) so 28A x 250% = 70A breaker
EGC: #8 here to match the ungrounded conductors right? Sized off 70A, but not to exceed ungrounded conductors 250.122(A).
Do these calculations look valid?
If a receptacle is the practicle solution, my question is with sizing it.The plug and receptacle are part of the wiring, so are they considered protected by the overloads? If so - 50A? If not, I don't see how you could size it from the OCPD at 70A.
I know I'm missing something here and just need a little guidance. Thanks in advance!
The equipment is on castors, so is it more common to install a plug on the cord with a receptacle? Or would hard-wiring be the preferred method?
What qualifies equipment or motors for cord and plug?
Would hard-wiring violate 400.8(1) or does this qualify for "frequent interchange" in 400.7(A)(6)?
For conductors: I've figured Table Amps (28A) X 125% = 35A. The conduit will have 7 current carrying conductors, so after derating 70%, it seems I need 3x#8 THHN.
For OCPD: It's fed out of a standard panel with a Cutler Hammer type BA breaker (inverse time right?) so 28A x 250% = 70A breaker
EGC: #8 here to match the ungrounded conductors right? Sized off 70A, but not to exceed ungrounded conductors 250.122(A).
Do these calculations look valid?
If a receptacle is the practicle solution, my question is with sizing it.The plug and receptacle are part of the wiring, so are they considered protected by the overloads? If so - 50A? If not, I don't see how you could size it from the OCPD at 70A.
I know I'm missing something here and just need a little guidance. Thanks in advance!