Ive lurked for a long time and decided to register to ask my question. I've got a few. First background of what I am doing.
I am sending power to a pumping station out near a creek in my backyard. Each pump is 1hp cap start wired for 240 volts. Running amps of both are roughly 21. I've already run direct burial xhhw 5 conductoropposed cable (4x8awg, 1x10 green for ground) Run is 200 ft.
My questions concern proper grounding, conductor usage and OCPD sizing.
I see 2 options:
w1 and w2 are both hots, w3 neutral and w4 or green as ground. Local ground rod bonded.
W1 and w2 on one pole, w3 and w4 on the other, no neutral and green for ground.
Nothing out there needs 120. Is option 2 legal?
As for the OCPD, I have a 30 amp gfci in the main panel. Is the gfci required even though i'I'm only running irrigation and not a pool? If I wire using option
I am sending power to a pumping station out near a creek in my backyard. Each pump is 1hp cap start wired for 240 volts. Running amps of both are roughly 21. I've already run direct burial xhhw 5 conductoropposed cable (4x8awg, 1x10 green for ground) Run is 200 ft.
My questions concern proper grounding, conductor usage and OCPD sizing.
I see 2 options:
w1 and w2 are both hots, w3 neutral and w4 or green as ground. Local ground rod bonded.
W1 and w2 on one pole, w3 and w4 on the other, no neutral and green for ground.
Nothing out there needs 120. Is option 2 legal?
As for the OCPD, I have a 30 amp gfci in the main panel. Is the gfci required even though i'I'm only running irrigation and not a pool? If I wire using option