however the other style where you wrap the wire can only have one per screw.
I wish everyone would stick to that. I have, and I am sure others have, seen as many as 4-14's wrapped around a screw
Follow up...You mean you can't put one wire in each of the holes on the back and another one wrapped around the screw?![]()
	The right size helps. Not the wire end... the terminal end. I'm fairly certain the screws are #8. The terminal end in picture would accommodate a #10. "They" do make different size terminal ends.... I have not yet seen a crimp connector that naturally fit under the screws; some modification or extreme deformation seems necessary.
No loops......however the other style where you wrap the wire can only have one per screw.
Clockwise?
Follow up...
Had to back the screw out a tad to get both back and front wires. BTW, those are #12.
No loops...![]()
I put it together for demonstration. Never, nor will it be, installed as such.Hope this was a 22.5 CUIN box!
The neutral only has to be pigtailed when it is part of a mutli-wire branch circuit.OK guys . . . we're going a little astray here. I think Dennis covered it earlier. Wirenutting the neutrals and a single white to the Duplex Receptacle and whatever is provided for the blacks - be it 2 screws, pressure plates or back stabs.
The positive leads do not have to be wirenutted. Thanks for the comments KO
Question on interpretation...The neutral only has to be pigtailed when it is part of a mutli-wire branch circuit.
Where a multiwire branch circuit has split off to a two-wire portion of the circuit, can the grounded conductor be connected through a receptacle's terminal(s)?