erickench
 - Brooklyn, NY
I have discovered what might be a peculiarity in the NEC. NEC 422.10(A) state's:
The rating of an individual branch circuit shall not be less than the marked rating of the appliance....
But NEC 422.11(E)(1) state's:
If the branch circuit supplies a single non-motor-operated appliance, the rating of the overcurrent protection shall comply with the following:
(1) Not exceed that marked on the appliance
From the above I would say that it would be impossible to have a marked continuous non-motor appliance on an individual circuit without violating the code.
Also, if the appliance were noncontinuous it could result in not being able to find an OCPD to match that on the marked rating because the marked rating would not be the same as a standard rating given in NEC 240.6. You would have to use an inverse time CB with a long time setting.
Does anyone care to comment on this?