anyone have a problem with installing a MB panel upside-down? the breaker switches horizontally (murray 200a).
I have a problem with everything.
240.33 Vertical Position. Enclosures for overcurrent devices
shall be mounted in a vertical position unless that is
shown to be impracticable. Circuit breaker enclosures shall be
permitted to be installed horizontally where the circuit breaker
is installed in accordance with 240.81. Listed busway plug-in
units shall be permitted to be mounted in orientations corresponding
to the busway mounting position.
enclosure is mounted in the vertical position
240.81 Indicating. Circuit breakers shall clearly indicate
whether they are in the open “off” or closed “on” position.
Where circuit breaker handles are operated vertically
rather than rotationally or horizontally, the “up” position of
the handle shall be the “on” position.
it doesn't seem like either of these references pertain to the issue.
circuit breaker operates horizontally.
the panel is mounted upside down not sideways.
I put the MB at the bottom quite often, haven't been flagged
looks funny if you're use to MB at the top
I had an inspector tell me one time that as long as the breaker didn't say "no" you were good!![]()
The only problem I could fore see about mounting it upside down, is if it were an outdoor rated panel. :happyyes:
what if it is installed indoors? is it OK? :happyno::happyyes::happysad:
Listing and labeling may come into the mix, but who reads that.The only problem I could fore see about mounting it upside down, is if it were an outdoor rated panel. :happyyes:
Could even work to one's advantage.Common in areas subject to flooding.
Silicone and duck tape can take care of a lot of those issues.Agree. A flipped 3R enclosure would be worthless.
	Mike for a panel with a main breaker that has the handle so that up is on I can agree with you as does the NEC, as in this photo of the original panel I removed at a house:
But most all breaker panels where all breakers are sideways switching including the main the NEC and UL clearly allows and even the manufactures have emboss printing in both directions as in this panel that I replaced the above panel with:
If you zoom in on the above photo you will see the word "LINE" embossed in both directions just below the main.
If directed at me I have no problem with a 'upside down' panel.
Oh I'm sorry as your post #2 seem to indicate other wise:?