I did a search but did not find the answer I need.
In the text book it shows to find the high leg of a 240/120 delta system find the square root of the line voltage squared minus the phase voltage squared.
On a 240 volt system this will equal 207.84 volts.
I have some electrical students that say the high leg in the plant where they are working is a lot higher than this. They say it is up as high as 219 volts.
How do I explain this to them? I have never seen a high leg on a 240 volt system that high in my entire experience. Could it be their meter is that far off and if it was wouldn?t it give a higher voltage than 240 and 120?
In the text book it shows to find the high leg of a 240/120 delta system find the square root of the line voltage squared minus the phase voltage squared.
On a 240 volt system this will equal 207.84 volts.
I have some electrical students that say the high leg in the plant where they are working is a lot higher than this. They say it is up as high as 219 volts.
How do I explain this to them? I have never seen a high leg on a 240 volt system that high in my entire experience. Could it be their meter is that far off and if it was wouldn?t it give a higher voltage than 240 and 120?