314.29--- but now i feel like I'm on the spot :ashamed1: :D

I guess i see the fixture "as part of the building" and the box not accessible since you must remove it (the light) to get at the 4 square and whip.
Perhaps I should rethink this?

I would rethink it. :)

Have you even installed a high hat in an inaccessible ceiling with no access from above which has a JB attached to it? You remove the fixture and the JB can be accessed. Same principal would apply to your installation. Something like this:

1104IC.jpg
 

plumb bob

Member
excellent point. my excuse :lol: is I expect to find that j-box at cans but was surprised when i saw this one above a 2x4 :lol:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For us old timers :roll: the JB adjacent to a florescent fixture in an inaccessible ceiling is nothing new. Back in the days before THHN and other 90? conductors we used TW. Since it was only rated for 60? C we would put in a JB above the ceiling and then run a 3/8" FMC whip into the fixture with higher temperature fixture wire.
 