I am trying to determine the AIC rating of a panel and the only thing I see is 100k EHD, What does EHD stand for ? Does that mean the Breaker has 100k AIC rating?
You appear to be asking a leading question often times in a way to get the answer that they want to hear.
If this is a service entrance there should be a the name of the manufacturer, the panel type and the nameplate/label on it which should include all of the ratings.
Often times the OP includes a smattering of info where we as respondents have to guess as to what you are getting at.
Your reference to a panel, you completely blew past who the panel manufacturer was, the type of panel and it’s nameplate with the ratings.
You mention EHD, you also stated 100K but completely failed to state who the manufacturer was, when there are KAIC ratings on the breaker there are also voltage ratings for each of them.
I'm going out on a limb and am going to ASSUME that the "EHD" being referred to in an Eaton, Cutler-Hammer, or Westinghouse breaker which are all in the same.
As such, this breaker is available in a 1,2, and 3p frame from 15 to 100AT. The 1p is rated for up to 277v, the 2 and 3p 480v. The KAIC ratings are 14 KAIC @ 277v, 18KAIC @240, and 14KAIC@480v.
Now, getting back to you OP "I am trying to determine the AIC rating of a panel and the only thing I see is 100k EHD, What does EHD stand for? Does that mean the Breaker has 100k AIC rating?"
Where does the 100K come in? When the the EHD breaker has a max of 18KAIC at 480v.