overcurrent protection for utility poles.

Status
Not open for further replies.

aelectricalman

Senior Member
Location
KY
Does anyone know the required fusing formula for cutouts, to protect a pole mounted cap bank ? Does it follow IEEE or is there another code body?

Would I have to acount for Inrush current and oversize for about 50% ish or is there a law of the land?
 
Last edited:

mivey

Senior Member
For a grounded wye bank:

Fuse link 100% rating = 1.35 * kvar_3ph / sqrt(3) / kV_LL

For a 150% rated fuse like a NEMA T-link, divide the current value above by 1.5

add:
For an ungrounded wye bank:

Fuse link 100% rating = 1.25 * kvar_3ph / sqrt(3) / kV_LL


The 25-35% adder comes from the normal allowance of:
10% for voltage
5%-15% for capacitor tolerance
5% for harmonics on ungrounded or 10% for harmonics on grounded wye
 
Last edited: