Ok, I have been trying to figure this job, the more I look at it the more confused and frustrated I get. I am licensed and SHOULD know how to do this. I am hoping you guys would please help, Im about to tell the customer I cant do it. I can do the work, just need some confidents in my numbers...
Feed: 480v 3phase bus, using 100a ITS switch fused at???Info says primary is 56a.
Trans: 45kva 480 Delta Primary, 400Y/231 secondary. says 68a max. This is a German press, they want me to adjust taps after we energize to get seconday voltage to 400v
Total Load: 47kVA
This press will operate 24/7, so I need to size my primary and secondary feeders 125% for continuous duty. Press has motors, heating elements....
Primary: 56a*1.25=70a= 3#4 and#6 ground in 1" emt
Seconday: 68a*1.25=85a=4#4 and #6 ground in 1 1/4 emt
Am I way off? What should Primary fuses be sized to? Am I correct in sizing to 125%?
Thanks....Frustrated