So I need to get 65kA in a panel that has some 20A breakers.
There are of course, no 20A breakers with a rating that high, even series rated. Unless one adds another breaker in the mix. Its like using a CB as a distribution block. It bugs me, but it is a workable and relatively inexpensive answer to the problem.