Ive got a job tomorrow to install a sub panel and receptacle for an irrigation system. My foreman wanted me to look up the code requirements for minimum distance from the creek to the panel (learning experience and all) but so far I am coming up confused. He also wanted me to look up information concerning grounding at the location. Here is what Ive found:
Article 682
Section III says nothing about needing a local ground rod connected to the local ground network or relying on the ground rod on the main panel at the house. 682.31(B) just says to carry a ground out there.
Section 682.11 says service equipment must be more than 5 feet from the bank. The planned location is 9 feet away.
Just wanting to make sure all my ducks are in a row before I show up and not look like a fool.