Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
At the first J-box where the circuit splits.
So not spliced and connect to each device? Thanks
At the first J-box where the circuit splits.
Short answer: generally anywhere the circuits branch off or are terminated at a load. For instance, if I ran two 480 circuits (3 ungrounded conductors each) for motor feeds, I would only splice the green #12AWG where the two circuits separated to each motor, and terminate each of those on a ring lug at each motor.
BTW, the note (as you quoted it in your OP) doesn't require a separate green ground conductor with each circuit, but only that the equipment grounding conductor be run with the branch circuits and feeders.
what would I do? I would run a green ground conductor in every conduit like it says to do.
is there a question here?
At the first J-box where the circuit splits.
Thanks Strat. So when running the ground from the ground bar in panel through the conduit with a few ckts where does the ground get connected/spliced to for say (3 ) ckts in that conduit?
The fact that you installed an additional grounding conductor does NOT mean that the metal conduit is NOT also a grounding conductor. Electrons do not know that they are supposed to travel on a wire instead of a pipe! Since the conduit is required to be "complete" in most cases, it is connected to the panel and to the equipment or outlet box, so it is indeed a grounding conductor, even if it is supplemented by a wire. If the waterline ground is "supplemented" by a ground rod, are they not both grounding electrodes?
What are you blind or just being dumb?
in light of your original post, i find this an
interesting response on your part.
Sorry, this thread is becoming a "how to" thread and it's time to close it.Thanks. So your saying that the ground would go to the loads? So if you had (5) single phase 120v circuits run out to a home run box and then pipes branch out from their to the circuits would there be a separate ground in each one of those " branch" conduits to the devices/loads or would it only be run to the HR box from the panel