ufer grounding

Status
Not open for further replies.

Rickyboothe

Member
Location
Amarillo Tx
Is it ok to connect a ufer ground to the sub panel grounding bar that contains the grounding conductor from the service disconect or do you have to go back all the way to the service disconnect
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The gec must go back to the main service assuming that this ufer is the main electrode for the building. In general, it will be installed to either the meter or the main service panel
 
Status
Not open for further replies.
Top