Raceways of different trade sizes connected together

Merry Christmas
Status
Not open for further replies.

dashburn

Member
Location
Crofton, MD
Is it allowed by NEC to connect different trade size raceways using a reducing fitting in the middle of a run? Example; 50' run of 1" RGS connected to 50' of 3/4" RGS using a reducing fitting in lieu of a box or condulet.
 
Yes, if conductor fill is sized for smallest raceway
But:
Makes pulling hard as you will hang up.
The next person will say, hey we have a 1" conduit here, lets go with more wires.
 