I was looking at a particular application wondering whether it is NEC compliant.
In a panel there is a 110A breaker protecting a #4 cable which runs for 50ft feeding the input of a VFD. I believe that VFD has an input breaker but am not exactly sure what size.
Now I know that typically the 110A breaker cannot protect the #4 cable (would need to be 100A breaker max) however I am wondering if using the tap rule that the breaker at the input of the vfd can protect the cable. For instance if the breaker at the input of the VFD is an 100A or 80A breaker would this protect the #4 cable by means of the tap rule.
I know also that the feeder breaker and cable must be sized at 125% of the VFD rated input current.
In a panel there is a 110A breaker protecting a #4 cable which runs for 50ft feeding the input of a VFD. I believe that VFD has an input breaker but am not exactly sure what size.
Now I know that typically the 110A breaker cannot protect the #4 cable (would need to be 100A breaker max) however I am wondering if using the tap rule that the breaker at the input of the vfd can protect the cable. For instance if the breaker at the input of the VFD is an 100A or 80A breaker would this protect the #4 cable by means of the tap rule.
I know also that the feeder breaker and cable must be sized at 125% of the VFD rated input current.