Just about the only transformers that are not SDS's are autotransformers.
The text in blue was added to the 2011 code to make it clear that you can have a connection between the primary and secondary via the EGCs and still have an SDS. Prior to that change, many code users skipped over the fact the the definition said you can't have a direct connection of a circuit conductor to the other system. The EGCs are not circuit conductors.Separately Derived System. A premises wiring system whose power is derived from a source of electric energy or equipment other than a service. Such systems have no direct connection from circuit conductors of one system to circuit conductors of another system, other than connections through the earth, metal enclosures, metallic raceways, or equipment grounding conductors.
I think there is a lot of confusion becuase a transformer will have a direct physical path between the grounded conductor of the primary and the grounded conductor of the secondary, assuming that both are grounded systems.
Buck/boost type are basically an isolation transformer connected as an autotransformer... and as such would not be an SDS.forgot about them. don't use them real often.
One example I can think of that is neither an autotransformer nor an SDS is a pad mount "service" transformer. To clarify, the transformer is consumer owned, so technically not a service transformer... but it is connected the same as a service transformer, where the primary and secondary neutrals are connected.I agree that the change in 2011 gives more clarification. ...
Quite true... but that has nothing to do with the requirement. The primary neutral is a circuit conductor as is the secondary neutral conductor. Connected to each other disqualifies it as an SDS.The primary and secondary neutrals are connected but not dependent on each other for the operation. If you had a 7.2 kV x 120/240 unit and removed the bond between primary and secondary, and still supplied the primary with 7.2 kV the secondary will still output 120/240 and will not care what or if anything is grounded.
There is no difference. The difference when talking SDS is the intended use of those conductors.I really don't see the elecrical difference between two white wires that are connected together and two green wires that are each connected to their associated white wire and then connected together.
Electrical color blindI really don't see the elecrical difference between two white wires that are connected together and two green wires that are each connected to their associated white wire and then connected together.
Electrical color blind:lol: