Ok. I have an odd scenario made even odder by having to put in a generator whole house auto backup in.
Here is the current setup. Service 4 ft underground to old 6"x6"x4" jbox (1930's) original. It is then nippled out to a 150 amp main disconnect. From there the load out goes to meter via 2/0 SER and out of meter SER back to a MLO then to another sub panel off that with #4 SER.
Ok. First of all, is that even code? I did not even open meter yet but would the installed have had to put in an isolated neutral bar in meter enclosure and is that even allowed?
Secondly, because I'd rather not deal with POCO for a shutdown at street can I add an automatic transfer switch on load side of 150 amp main disconnect via nipple, then add isolated neutral bar in autotransfer switch?
I understand everything downstream of main is now a sub panel and needs an isolated neutral but not sure how this pertains to meters and automatic transfer switches.
Here is the current setup. Service 4 ft underground to old 6"x6"x4" jbox (1930's) original. It is then nippled out to a 150 amp main disconnect. From there the load out goes to meter via 2/0 SER and out of meter SER back to a MLO then to another sub panel off that with #4 SER.
Ok. First of all, is that even code? I did not even open meter yet but would the installed have had to put in an isolated neutral bar in meter enclosure and is that even allowed?
Secondly, because I'd rather not deal with POCO for a shutdown at street can I add an automatic transfer switch on load side of 150 amp main disconnect via nipple, then add isolated neutral bar in autotransfer switch?
I understand everything downstream of main is now a sub panel and needs an isolated neutral but not sure how this pertains to meters and automatic transfer switches.