334.30 - TIP
jxofaltrds
Retired ESI
Mike P. Columbus Ohio
Creator
A few years back in a old farm house remodel I had to run NM in a new soffit. No way to use staples, no room for a hammer, so I used zip ties. NM no where near being subject to damage. Failed inspection by a fellow ESI buddy, thanx Karl. Zip ties not approved. So as not to be beat I found a trick to use staples on the flat side of a 2X4.
334.30 Securing and Supporting. Nonmetallic-sheathed
cable shall be supported and secured by staples, cable ties,
straps, hangers, or similar fittings designed and installed so
as not to damage the cable, at intervals not exceeding 1.4 m
(41⁄2 ft) and within 300 mm (12 in.) of every outlet box,
junction box, cabinet, or fitting. Flat cables shall not be
stapled on edge.
Sections of cable protected from physical damage by raceway
shall not be required to be secured within the raceway.
I open these channel locks (LARGE) and was able to squeeze the staples into the stub. I know he still does not not how I did it. LOL :p
You can staple to the 'backside' of a stud this way!
Try it and let me know. It will drive your fellow electricans nuts to figure out how you did it (staple).
Nice ... but I thought cable ties = zip ties? .... just use the jacket off NM it has UL stamped all over it!:D
I have used channel locks to nail a 1096 down before, same principle open wide grab the nail on box and other side of stud ... just squeeze
worked fine for tight locations