Hello everyone newbie here,
I have always worked on single family homes and am working on my first multi family home project.
The Building has one house panel, three apartments each with
*Electric heat (heat pump)
*Electric Hot water
*8 kw range
*Electric Dryer
*Misc exhaust fans etc.
*Standard 3 VA general load, 2 appliance, 1 laundry
AND there is a 3600 sf detached warehouse being fed from this service
The service to the building is three phase 120/208
each dwelling unit will have 120/208 single phase
the warehouse will have 120/208 three phase
I have never had to do a calculation for a multi family home and am wondering how to go about sizing the "house panel"
in CT we are still on the 2005 NEC. article 220.84 says the house loads shall be calculated in accordance with part three.
Do i take the common area square footage to get the general lighting load? Do i still need to have small appliance circuits etc or just the connected loads?
I also noticed in 220.55 it states that "where two or more single-phase ranges are supplied by a 3-phase, 4wire feeder or service the total load shall be calculated on the basis of twice the maximum number connected between any two phases" . Does this mean I need to double the calculated size? for example if I have a range on A & B, one on B & C and one on A & C each range is 8kw I need to calculate each range at 16 kw before the demand factor adjustment?
Another question i have is for sizing feeders for the individual units. I'm assuming those feeder are sized at 100% and no demand factors are to be used, is this correct?
Thank you in advanced for any help
Best Regards,
Jon
I have always worked on single family homes and am working on my first multi family home project.
The Building has one house panel, three apartments each with
*Electric heat (heat pump)
*Electric Hot water
*8 kw range
*Electric Dryer
*Misc exhaust fans etc.
*Standard 3 VA general load, 2 appliance, 1 laundry
AND there is a 3600 sf detached warehouse being fed from this service
The service to the building is three phase 120/208
each dwelling unit will have 120/208 single phase
the warehouse will have 120/208 three phase
I have never had to do a calculation for a multi family home and am wondering how to go about sizing the "house panel"
in CT we are still on the 2005 NEC. article 220.84 says the house loads shall be calculated in accordance with part three.
Do i take the common area square footage to get the general lighting load? Do i still need to have small appliance circuits etc or just the connected loads?
I also noticed in 220.55 it states that "where two or more single-phase ranges are supplied by a 3-phase, 4wire feeder or service the total load shall be calculated on the basis of twice the maximum number connected between any two phases" . Does this mean I need to double the calculated size? for example if I have a range on A & B, one on B & C and one on A & C each range is 8kw I need to calculate each range at 16 kw before the demand factor adjustment?
Another question i have is for sizing feeders for the individual units. I'm assuming those feeder are sized at 100% and no demand factors are to be used, is this correct?
Thank you in advanced for any help