derating question more then 3 conductors in conduit

Status
Not open for further replies.

grumpy11

Senior Member
4 # 1/0 to 150 amp circuit breaker using 90 degree wire 1/0 rateing is 170 amps.

if i derate 80% the rating is now 136 amps. to small a rating for 150 amp,

does this sound right.

i think i should use 2/0 90 degree at 195 amps x 80% is 156 amps.

any comments.
 

jumper

Senior Member
SO THE WIRE SIZE SHOULD BE 2/0 correct

I think 3/0. Not sure.:(

207ecm24fig2.jpg


http://ecmweb.com/content/transformer-installation-made-easysort
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
so the 4 conductors have to be derated
We don't know that yet, because you have not told us what type of load is being served. The grounded conductor would be counted as a current carrying conductor only if the major portion of the load is non-linear.
 

kwired

Electron manager
Location
NE Nebraska
lets say it does it feeds a panel that feed outlets

That does not help much, what kind of loads connected to the outlets? When talking NEC terms an outlet is "A point on the wiring system at which current is taken to supply utilization equipment". Pretty much all branch circuits supply at least one "outlet"
 