nhfire77

Senior Member
Location
NH
Anyone have a manual for this?

Does anyone know if, when in phone line trouble why it reports SI248, equipment failure?

Is it because of the telco trouble or is that another fatal flaw?
 

nhfire77

Senior Member
Location
NH
More info

More info

The raw data was IA 6 (SIA format). Which is System trouble comm fault typically.

I'm more concerned with it not reporting off normal every other day with the comm fault.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Anyone have a manual for this?

Does anyone know if, when in phone line trouble why it reports SI248, equipment failure?

Is it because of the telco trouble or is that another fatal flaw?

Usually it's a telco issue; low/no voltage on the line. Sometimes the PBX "analog" port doesn't agree with the modem.
 

nhfire77

Senior Member
Location
NH
Usually it's a telco issue; low/no voltage on the line. Sometimes the PBX "analog" port doesn't agree with the modem.

yes, the line was disconnected. Since I couldnt get a keypad to hook up to it and see the trouble I wanted to make sure it hadn't gone bad. Its a tenant landlord issue now. Thank you.
 