Sir Ohms-A-Lot
- Huntsville, AL, USA
I went to Lowe's today to get a feeder for a single-phase 100 amp load center.
We usually use copper in the field & I knew off hand that I could use #3 AWG, but since I was on a side job I looked in the code book for the Al size of equal or greater ampacity.
I was of the opinion that I should use the 75 degree C column of 310.16, since my breaker will not be rated any higher, and I came up with #1 AWG Aluminum for 100 amps.
I was surprised when I went to Lowe's that they didn't have any of those triplex cables with #1 Al; it was all #2.
So then the guy tells me that #2 is what I want for a 100 amp feeder, and I'm guessing I must be missing something, cause surely Lowe's wouldn't be pushing smaller than code sizes of wire off on folks.
Is there some note in the code that allows a smaller size than the ampacity table shows?
I saw a note like that once that allows #2/0 Cu for a 200 amp service if it is a single dwelling unit. Is this something like that?