900 Amp 480/277v Y Service

Status
Not open for further replies.

jap

Senior Member
Occupation
Electrician
Would it be safe to assume that a 1200 Amp 480v/277 Y 3r Fused Service Disconnect Switch Fused at 900 amps would relieve you of the GFI requirement of 1000 amps and above?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
It is never safe to assume anything. In this case, it would be a particularly poor assumption. The beginning of the second paragraph of 230.95 says that the rating of a fused service disconnecting means is the highest size fuse that can be installed. So your installation would exceed the 1000 amp threshold, even though you used 900 amp fuses.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Would it be safe to assume that a 1200 Amp 480v/277 Y 3r Fused Service Disconnect Switch Fused at 900 amps would relieve you of the GFI requirement of 1000 amps and above?

not if it is a service.
230.95 Ground-Fault Protection of Equipment. Groundfault
protection of equipment shall be provided for solidly
grounded wye electric services of more than 150 volts to
ground but not exceeding 600 volts phase-to-phase for each
service disconnect rated 1000 amperes or more. The
grounded conductor for the solidly grounded wye system
shall be connected directly to ground through a grounding
electrode system, as specified in 250.50, without inserting
any resistor or impedance device.
The rating of the service disconnect shall be considered
to be the rating of the largest fuse that can be installed or
the highest continuous current trip setting for which the
actual overcurrent device installed in a circuit breaker is
rated or can be adjusted.

beat me to it. but if it is just a feeder, it would seem to be ok.

just out of curiousity, how does one provide GF protection on a fuse?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
It is never safe to assume anything. In this case, it would be a particularly poor assumption. The beginning of the second paragraph of 230.95 says that the rating of a fused service disconnecting means is the highest size fuse that can be installed. So your installation would exceed the 1000 amp threshold, even though you used 900 amp fuses.

Just as a thought...what does "highest fuse that can be installed" mean. Does it mean that largest fuse that can be physically installed in the switch, ie, 1200A in the OP's switch...

or does it mean the largest fuse that can legally be installed to provided the code required overcurrent protection?

For instance, if the OP's installation had service conductors that were 3 sets of 350mcm (total ampacity of 930.) Installing 1000A fuses in the switch would violate 230.90(A). Would that make 900A the largest fuses that "can" be installed?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Install an enclosed circuit breaker in series, and include the GFI protection on it? :lol:

I have always found this to be a curious requirement, since it basically seems to require Wye feeders and services of 1000A or more to be CB, while nominally allowing fuses.

I have often wondered what the thinking is with this requirement. Why are grounded delta systems excluded? Why are ungrounded delta systems excluded?

why are 208/120 systems excluded?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
...
why are 208/120 systems excluded?
I have been taught it is because an arcing ground fault is not sustainable (does not restrike after zero crossing) on a 208/120Y system, but it is on a 480/277Y system. The arcing fault can produce enough heat to melt the switch gear down without tripping the OCPD unless it has GFP.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
not if it is a service.


beat me to it. but if it is just a feeder, it would seem to be ok.

just out of curiousity, how does one provide GF protection on a fuse?

In the old days, a CT would encompass the conductors, which with the help of a relay trigger a shunt trip solenoid Of course this only works with a spring loaded switch.
 
Last edited:

zog

Senior Member
Location
Charlotte, NC

jap

Senior Member
Occupation
Electrician
The Reason I ask is because the engineer designed a particular project with a 1000A 480/277v Y Service.
A 1000a 480v Enclosed 3r GFI Breaker was quoted and submitted.
The Engineer rejected the submittals indicating that the rule applied to "Above" 1000 amps.
We argued the fact that it was 1000 amps and above.
A temporary generator was coming in to power the facility while the Existing Padmount could be relocated and they needed a Disconnect to put in place where the GFI Enclosed Breaker (That got rejcted) was going to go.(The Pipes were already roughed in to this location).
They requested a 1000a Fused Disconnect. (Which is a 1200 Amp Disc with 1000A Fuses).
The Temp Gen has a GFI Output breaker Feeding the Temp Disconnect, which is ok for now.
But once the Temp Generator gets taken off line, I dont see any way around not having to replace the Fused Disconnect. The 900a Fuse Option came up but evidently the clause in the code rule would not allow this either.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
The Engineer rejected the submittals indicating that the rule applied to "Above" 1000 amps.
That engineer needs to get a lesson on "Charlie's Rule." The code says what it says, not what anyone (engineers included) thinks it says. The actual text is quoted in post 3 above, and it clearly says, "1000 amps or more."
But once the Temp Generator gets taken off line, I dont see any way around not having to replace the Fused Disconnect. The 900a Fuse Option came up but evidently the clause in the code rule would not allow this either.
I have to agree with you. But you need to get the engineer to wake up to the fact that your original submittal correctly included the GFI feature.
 

zog

Senior Member
Location
Charlotte, NC
From the part that I can access, it appears to be talking about 277 volt arcing faults, and I agree that those re-strike, and that is the very reason for the ground fault protection rule, but I was trying to say that the 120 arcing ground faults do not re-strike and that is why GFP is not required on 208/120Y systems.

You need to read the entire study, this was done to conduct research specifically on 208/120V systems to settle that arguement from IEEE 1584 ommiting 208/120 systems from arc flash analysis requirements, which was then removed from 70E after this research showed sustainable arcing faults to ground on 208/120V systems.
 

zog

Senior Member
Location
Charlotte, NC
Zog -
This was published in 1977. Did I miss something about how recent this is? A lot of my work concerns Arc flash. I'm definitely interested if there is new data.

ice

SOB, I posted wrong link. The 2012 70E removed the 208/120V <125kVA exception based on ongoing IEEE research, but now I can't find that link. I know the IEEE 1584 commitee has some new data on this and those studies were based off a 2004 PG&E study that suggested a 120V arc can self sustain for >1 second so they backed off that exception. I have a super busy day ahead of me but will try and find new study link Friday.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You need to read the entire study, this was done to conduct research specifically on 208/120V systems to settle that arguement from IEEE 1584 ommiting 208/120 systems from arc flash analysis requirements, which was then removed from 70E after this research showed sustainable arcing faults to ground on 208/120V systems.
I don't have any access to the entire study. It does not appear to be available to me without cost.

There was some discussion of this on one of the recent AFCI threads saying that at sustainable series arc on a 120/240 system is not possible.

If there really is the possibility of an "acring burndown" on a 208/120Y system like there is for a 480/277Y system, why does the code only require GFP protection for the 480/277Y system?
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
... If there really is the possibility of an "acring burndown" on a 208/120Y system like there is for a 480/277Y system, why does the code only require GFP protection for the 480/277Y system?

I don't know that 208Y is particularly in danger. Here is an excerpt from the latest rev of IEEE 1584:

It was difficult to sustain an arc at the lower voltages. An arc was sustained only once at 208 V in a 508 mm? 508 mm ? 508 mm box. In all other tests with that box and the 305 mm ? 368 mm ? 191 mm box, the arc blew itself out as soon as the fuse wire vaporized. An arc was sustained several times at 215 V in a device box (100 mm ? 100 mm ? 50 mm size). It appeared from the arc-flash photos from the
305 mm ? 368 mm ? 191 mm box that testing arcs usually jumped from the electrodes to the box wall and
from another point on the box wall back to another electrode. The magnetic forces created by these arc
currents forced them away from each other and into the box wall.

Arc faults can be sustained at 208 V and have caused severe injuries with very high short-circuit current
applications in meter enclosures. A meter enclosure is small and tends to confine an arc more than laboratory test boxes with no door. Used equipment at 208 V was not tested, but it is recognized that many types of equipment have relatively small open spaces between components, such as the space in a panelboard between the circuit breakers and the wall of the enclosure.

While the accuracy of the model at 208 V is not in the same class with the accuracy at 250 V and higher, it
will work and will yield conservative results. The arc-flash hazard need only be considered for large 208 V
systems: systems fed by transformers smaller than 125 kVA should not be a concern.

As to why the NEC doesn't recognize 208 systems, probably because the danger is with small, high SCC, meter boxes - not particularly with normal sized switchgear boxes.

And, of course, 90.1.A, "practical safeguarding", not perfect safeguarding.

ice
 

cmcj1975

New User
Location
Houston, TX
So installing a 1200 amp main lug only switchboard and dividing up the feeders to not exceed 1000 amps (staying 6 switches or less) is ok? I guess as long as it would be physically impossible to put anything 1000 amps or larger in it?
 
So installing a 1200 amp main lug only switchboard and dividing up the feeders to not exceed 1000 amps (staying 6 switches or less) is ok? I guess as long as it would be physically impossible to put anything 1000 amps or larger in it?

Doing this is very commonly used to get around the GFPE requirement. A 1000 amp MLO panelboard with 6 breakers is about 5K, twice that to add a main, and that's 208 gear without GFP.

There is no requirement that it be set up such that a 1000 amp or more breaker cannot be installed.
 