non grounded system extension

Status
Not open for further replies.

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
I was thinking about this today, can EMT be used to extend a non grounded system? It is in a residential garage lighting outlet and the customer wants it extended to another point and it will be done with EMT. Now my concern is if the system is not grounded, how is this safe?
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
A metal face plate as required by code has to be connected to an EGC.
Now, what is the difference between this installation and the installation that i have originally posted. Of course besides the obvious one is face plate one is EMT.
 

Smart $

Esteemed Member
Location
Ohio
A metal face plate as required by code has to be connected to an EGC.
Now, what is the difference between this installation and the installation that i have originally posted. Of course besides the obvious one is face plate one is EMT.
This is...

250.86 Other Conductor Enclosures and Raceways.
Except as permitted by 250.112(I), metal enclosures and raceways
for other than service conductors shall be connected
to the equipment grounding conductor.

Exception No. 1: Metal enclosures and raceways for conductors
added to existing installations of open wire, knoband-
tube wiring, and nonmetallic-sheathed cable shall not
be required to be connected to the equipment grounding
conductor where these enclosures or wiring methods comply
with (1) through (4) as follows:
(1) Do not provide an equipment ground
(2) Are in runs of less than 7.5 m (25 ft)
(3) Are free from probable contact with ground, grounded
metal, metal lath, or other conductive material
(4) Are guarded against contact by persons

Exception No. 2: Short sections of metal enclosures or

raceways used to provide support or protection of cable
assemblies from physical damage shall not be required to
be connected to the equipment grounding conductor.

Exception No. 3: A metal elbow shall not be required to be
connected to the equipment grounding conductor where it
is installed in a run of nonmetallic raceway and is isolated
from possible contact by a minimum cover of 450 mm
(18 in.) to any part of the elbow or is encased in not less
than 50 mm (2 in.) of concrete.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
I was thinking about this today, can EMT be used to extend a non grounded system? It is in a residential garage lighting outlet and the customer wants it extended to another point and it will be done with EMT. Now my concern is if the system is not grounded, how is this safe?

NOTE: No EGC being added.

It seems that 250.130(C) would disagree with you.

See above NOTE so 130(C) does not apply.

This is...


Exception No. 1: Metal enclosures and raceways for conductors
added to existing installations of open wire, knoband-
tube wiring, and nonmetallic-sheathed cable shall not
be required to be connected to the equipment grounding
conductor where these enclosures or wiring methods comply
with (1) through (4) as follows:
(1) Do not provide an equipment ground
(2) Are in runs of less than 7.5 m (25 ft)
(3) Are free from probable contact with ground, grounded
metal, metal lath, or other conductive material
(4) Are guarded against contact by persons

He is extending not adding.
I assumed that it is not guarded.
 

Smart $

Esteemed Member
Location
Ohio
...

He is extending not adding.
I assumed that it is not guarded.
Logic precludes extending is adding.

May not be guarded now, or not planned to be... but now being aware of that requirement, it can be made to be guarded, or plans altered accordingly.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
NOTE: No EGC being added.



See above NOTE so 130(C) does not apply.




Exception No. 1: Metal enclosures and raceways for conductors
added to existing installations of open wire, knoband-
tube wiring, and nonmetallic-sheathed cable shall not
be required to be connected to the equipment grounding
conductor where these enclosures or wiring methods comply
with (1) through (4) as follows:
(1) Do not provide an equipment ground
(2) Are in runs of less than 7.5 m (25 ft)
(3) Are free from probable contact with ground, grounded
metal, metal lath, or other conductive material
(4) Are guarded against contact by persons

What does it mean "Guarded against contact..." i need to build a nonconductive enclosure around it? Above 7', 8', 10'... is considered guarded??

Does the installation have to comply with ALL of 1 through 4 or only one of the 4 requirements?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What does it mean "Guarded against contact..." i need to build a nonconductive enclosure around it? Above 7', 8', 10'... is considered guarded??

Does the installation have to comply with ALL of 1 through 4 or only one of the 4 requirements?

I think this means if an individual can come in contact with it then it must be grounded. Perhaps there are situations where there is no need for an egc so you can extend it but it must be protected or guarded so that persons cannot come in contact with the device.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
What does it mean "Guarded against contact..." i need to build a nonconductive enclosure around it? Above 7', 8', 10'... is considered guarded??

Does the installation have to comply with ALL of 1 through 4 or only one of the 4 requirements?

All 4.

I think this means if an individual can come in contact with it then it must be grounded. Perhaps there are situations where there is no need for an egc so you can extend it but it must be protected or guarded so that persons cannot come in contact with the device.
I agree.
 