jcbabb
Member
- Location
- Norman, OK, USA
I have a project where we designed a new softball and football playing field for a high school. The state fire marshal mentioned in his plan review comments that "emergency egress lighting is required for all exit paths per the IBC paragraph 1006.3. This is for the new football bleachers and the softball bleachers."
I questioned his requirement for emergency lighting based on my reading of the code. In a clarification response, he further stated that "it is required by code for any path of egress to be illuminated for safe egress to the public way. This would include the steps going up the bleachers to the seating area as well as the ramps and sidewalks leading to the public way".
I don't see how the IBC 1006.3 requires emergency lighting for this type of installation. Am I just reading it incorrectly? I want to be code compliant, but at the same time I need to be budget conscious. There are over 1000' of sidewalks between the bleachers and the "public way". Providing emergency lighting for these paths would be a significant cost.
Have any of you encountered this requirement?
Thanks for your input!
I questioned his requirement for emergency lighting based on my reading of the code. In a clarification response, he further stated that "it is required by code for any path of egress to be illuminated for safe egress to the public way. This would include the steps going up the bleachers to the seating area as well as the ramps and sidewalks leading to the public way".
I don't see how the IBC 1006.3 requires emergency lighting for this type of installation. Am I just reading it incorrectly? I want to be code compliant, but at the same time I need to be budget conscious. There are over 1000' of sidewalks between the bleachers and the "public way". Providing emergency lighting for these paths would be a significant cost.
Have any of you encountered this requirement?
Thanks for your input!