Hi all and TIA --
I have searched and can't seem to find an answer so here goes--
I was asked to look at a problem in a friends new house(he's building it). He had Journeyman friend of his wire it-- and they don't have an answer either---
Ok problem:
Two bedrooms with the same problem-- Each bedroom on a single circuit--recepts and lighting--1 room has 3 Commercial IEC rated cans and the other has 2--Close the AFCI breaker and all is fine--turn on a light or plug something into the recept and the AFCI trips--does not matter what the load is--anytime it comes under load it trips.
We have hand over handed the runs from panel to the end--nothing is stapled too tight and all connections are good, even megged it out--500Mohms plus(L-N,L-G,N-G, all ends floated and not touching anything). He was using CFLs at first-then went to incandescent--no change
It is a Square D Homeline panel-15A breakers-
Short of buying new breakers-- is there anything I missed?? Got me stumped-
Sorry if this is a bit disjointed but it's 0400 and I have just pulled a double and a half so I am a weee bit tired
As always--Thanks all!!
Rich
I have searched and can't seem to find an answer so here goes--
I was asked to look at a problem in a friends new house(he's building it). He had Journeyman friend of his wire it-- and they don't have an answer either---
Ok problem:
Two bedrooms with the same problem-- Each bedroom on a single circuit--recepts and lighting--1 room has 3 Commercial IEC rated cans and the other has 2--Close the AFCI breaker and all is fine--turn on a light or plug something into the recept and the AFCI trips--does not matter what the load is--anytime it comes under load it trips.
We have hand over handed the runs from panel to the end--nothing is stapled too tight and all connections are good, even megged it out--500Mohms plus(L-N,L-G,N-G, all ends floated and not touching anything). He was using CFLs at first-then went to incandescent--no change
It is a Square D Homeline panel-15A breakers-
Short of buying new breakers-- is there anything I missed?? Got me stumped-
Sorry if this is a bit disjointed but it's 0400 and I have just pulled a double and a half so I am a weee bit tired
As always--Thanks all!!
Rich