wtrski
 - Mount Bethel, PA
Our facility is building a new Summer staff building which the engineer spec'd out a 600 Amp 3phase service. my load calculations came up with the ability to use a 400 Amp peak 320 amp 3 phase continuous service for this location from our electrical provider. Now the engineer shows that i am to come off this meter base to a 400 amp Main panelboard in our utility room which will feed over to 2 -200 amp sub panelboards. 1 panelboard in each wing of the building (guys side & girls side). I am also supposed to come off this meter with a 100 amp service to the Fire pump enclosure buried outside in a pit containing a 15 hp Fire Pump and a small jockey pump along with some controls.
My questions for you are as follows
1. do i need a breaker type disconnect at the meter base before running to both the 400 amp main panel and also the 100 amp fire pump enclosure?
2. The engineer showed that i am to use MLO Panels for the sub panels. Am i not required to have a main breaker in these sub panel's. it will be breakered at the main panel but my inspector has argued in the past that if the main disconnecting means is not in sight of the sub panel then a means of disconnect must be installed hence neeeding a panel with main breaker.
3. how should i go about feeding these two seperate services from the Meter base. should i bring the service from the meter base into a CT cabinet to use as a splice point to feed each service (main panel & Fire Pump enclosure) or should i just come off the Meterbase with each service.
4. is running 2- 4/0 THHN per phase & Neutral in 2-3" conduits adequate for this installation? Is a #2 GEC to 2 ground rods 6 feet apart bonded together appropriate.