Installation - 4 parallel runs of 600 KcMil Copper in a short section (<4') of Aluminum Cable Tray between a 2MVA transformer and Switchgear. To accommodate existing transformer taps. The 16) 600 KcMil must enter the top of the transformer through a insulating panel, in an "isolated phase" installation. When parallel conductors are installed in a cable tray NEC 392.8(D) require them to be installed, securely bound in circuit groups in order to prevent current imbalance due to inductive reactance.
Problem; in order to install the 16) KcMil CU in an isolated phase fashion it is impractical to bundle the circuit conductors together on such a short piece of cable tray. The individual conductors have been laid out as single conductors and securly bound to the cable tray to prevent excessive movement during a fault; as follows AAAABBBBCCCCNNNN.
Question; How much of an issue is current imbalance on such a short piece of aluminum cable tray?
Problem; in order to install the 16) KcMil CU in an isolated phase fashion it is impractical to bundle the circuit conductors together on such a short piece of cable tray. The individual conductors have been laid out as single conductors and securly bound to the cable tray to prevent excessive movement during a fault; as follows AAAABBBBCCCCNNNN.
Question; How much of an issue is current imbalance on such a short piece of aluminum cable tray?