johnsciolino
- Jacksonville, Fl
The local inspector is telling us that a 2X4 Luminaire needs to have the whip changed to HCA Healthcare Cable
The Article mentioned above states if over 7-1/2', its not required. He is saying that it has to be outside the patient care area just like the switch.
Sounds to me like a reading comprehension problem.
Your thoughts?
Exact verbiage:
Luminaires more than 7-1/2' above the floor and switches located outside the patient care vicinity shall be permitted to be connected to an equipment grounding return patch complying with 517.13(A)
517.13(A) states that the conduit and/or grounding path shall qualify as an equipment grounding conductor in accordance with 250.118