2 4ton cac units 125' from panel.

Status
Not open for further replies.

stickboy1375

Senior Member
Location
Litchfield, CT
I'm going to run 4/2 nm.

I'd pull # 2/3 SER AL., just to cover my ass and charge accordingly because the specs were not present. Plus this gives options later on when they need to add something. Win/Win in my book. I bet i come out cheaper than the copper you propose to run.
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
I'd say #8CU would be more than adequate.

For supplying two units? Remember NM cable is also sized per 60oC ampacity tables.

Depending on just what the nameplates of the units say 6 AWG may work, but could be close to being too small, with 125 feet of length 4 AWG may be a good idea for voltage drop purposes even if 6 is acceptable for ampacity reasons.

I say this without any calculations other than simple ones from memory, but I think is fairly accurate. I know 6AWG @ 60oC is only good for 55 amps, so if MCA of units is over 27.5 amps you need to look pretty carefully before selecting 6 AWG NM cable.
 

aftershock

Senior Member
Location
Memphis, TN
For supplying two units? Remember NM cable is also sized per 60oC ampacity tables.

Depending on just what the nameplates of the units say 6 AWG may work, but could be close to being too small, with 125 feet of length 4 AWG may be a good idea for voltage drop purposes even if 6 is acceptable for ampacity reasons.

I say this without any calculations other than simple ones from memory, but I think is fairly accurate. I know 6AWG @ 60oC is only good for 55 amps, so if MCA of units is over 27.5 amps you need to look pretty carefully before selecting 6 AWG NM cable.

that is why I chose #4
 

aftershock

Senior Member
Location
Memphis, TN
Reason I brought this up is because of a TC. Same units, older house shorter run, but #6 was used and the units were tripping the 60 amp breaker. Now I am fixing to wire similar but longer run.
 